maypot
Electrical
- Feb 25, 2005
- 108
We got a breakdown on one of our 400 V variable speed drive yesterday morning. The drive tripped on starting and the following faults were recorded namely overcurrent,angu , ground fault, overvoltage and undervoltage . The motor was disconnected to the load and the motor started .It again tripped before starting and the same faults noted.After some attempts, it finally ran and at 40 Hz ,the current on the first and second phases were 480 A but the current on the third phase was only around 240 A. The output module of the third phase has been dismounted but the IGBT appears to be fine, with no apparent short or open circuit. We are suspecting the firing card.There are four IGBTS on each phase and if two IGBTs were not firing, I understand that the drive would trip on overcurrent but ground fault and over and under voltage trips seem strange.
Grateful to have some inputs on your side.
Bob
Grateful to have some inputs on your side.
Bob