My guess would be breaker failure thats done by the bus protection. The 487B is capable to doing such. Some POCOs use the 52a contact in breaker failure protection and others do not. Ie, 52a or 50BFP will trigger a BF trip, for others 52a and 50BFP= BFT, yet for others just current is used. Each has its own advantage or disadvantage. *And* logic is more secure, but can miss certain breaker failures; while *or* logic is less secure but is best used for transformers or anywhere current may be below the 50BF pickup. There are other reasons like SCADA, MOD switching, ect, ect.
What are you doing or is being done?