SouthSide08
Electrical
- Apr 4, 2017
- 11
I'm curious to understand how others have determined the ampacity for sizing feeder cables to a 48Vdc control circuit of a 138kV HV circuit breaker. I have the information for the loads in the control circuit in which largest loads are the 2-trip coils and 1-open coil. All other loads (trip coil monitor, undervoltage relays, indicating lights, etc.) are non-significant in terms of load size. I have the information on the trip coils and open coil running duration, which is momentary (less than 1 secs). I believe that I don't have to consider these loads for my ampacity calculations since these aren't considered continuous. I see it similar to not sizing a motor feeder per the motor starting current. I would like to see some precedent or if there is something I may have missed. Appreciate y'alls comment in advance!