I'm an EE working on a planned multistory 3800ft^2 residence in Northern CA.
The house must have sprinklers running off a single combined domestic/fire pump. I'm trying to SWAG the needed capacity for pump & power planning purposes. We are 6-8 months away from a sprinkler designer.
The house will have >10Kgals of potable storage, with 20 feet of positive head.
NFPA 13D < talks about water supply in Chap. 6.
Specifically, 6.1.3 states the quantity is at least 7 minutes times "the two sprinkler demand rate" unless the house is bigger than one story or 2kft^2.
I do not find a direct statement as to the required flow rate from the water system. I do find in 8.1.1.1.1 that the system must be able to provide 13pgm simultaneously to all sprinklers. (That's a LOT of water! With say 40 sprinklers... I must not be understanding it correctly....)
a) What does 8.1.1.1.1 mean?
b) Is there a direct statement re: required flow? If it is "two sprinklers" then a 1200 ft^2 house and a 4500 one would need the same pump.....
c) 6.1.3. addresses houses smaller than this one; what applies here?
d) The usual approach to meeting the varying pump demand is a variable frequency drive feeding the pump motor. (One brand name I find is "Aquaboost") But this house will be fed with 208/3ph. Has anyone found a VFD controller that accepts 3ph? [Yes, we could run it off of the 208, but that's a topic not 100% germane to this forum...]
e) The owner asked about external connections; so an outdoor pump could be used when the power is down. (CalFire requires a Emergency Power Off on the outside wall. But using it kills the fire pump...) Commercial building sprinklers have those for FD connections; has anyone seen such on a house?
The house must have sprinklers running off a single combined domestic/fire pump. I'm trying to SWAG the needed capacity for pump & power planning purposes. We are 6-8 months away from a sprinkler designer.
The house will have >10Kgals of potable storage, with 20 feet of positive head.
NFPA 13D < talks about water supply in Chap. 6.
Specifically, 6.1.3 states the quantity is at least 7 minutes times "the two sprinkler demand rate" unless the house is bigger than one story or 2kft^2.
I do not find a direct statement as to the required flow rate from the water system. I do find in 8.1.1.1.1 that the system must be able to provide 13pgm simultaneously to all sprinklers. (That's a LOT of water! With say 40 sprinklers... I must not be understanding it correctly....)
a) What does 8.1.1.1.1 mean?
b) Is there a direct statement re: required flow? If it is "two sprinklers" then a 1200 ft^2 house and a 4500 one would need the same pump.....
c) 6.1.3. addresses houses smaller than this one; what applies here?
d) The usual approach to meeting the varying pump demand is a variable frequency drive feeding the pump motor. (One brand name I find is "Aquaboost") But this house will be fed with 208/3ph. Has anyone found a VFD controller that accepts 3ph? [Yes, we could run it off of the 208, but that's a topic not 100% germane to this forum...]
e) The owner asked about external connections; so an outdoor pump could be used when the power is down. (CalFire requires a Emergency Power Off on the outside wall. But using it kills the fire pump...) Commercial building sprinklers have those for FD connections; has anyone seen such on a house?