ThePunisher
Electrical
- Nov 7, 2009
- 384
We have a case at site where the the 100:5A, C20, ABB BYZ-S ZCT window was accommodating 2 per phase power cables and due to the window size the phase A and Phase C cannot be terminated vertically straight but are naturally self-bending towards their terminals at almost 45 deg angle.
We thought of using a UL/CSA Listed 45 Deg-angled terminal block. We got confirmation from our switchgear vendor that the ZCT is fine. I have got our construction folks to measure the clearances using the angled terminal blocks and the clearances are still ok plus the terminations will be covered with additional re-usable insulating boots.
I do not see any issues using the 45 Deg terminals as it matches the natural bend of the cable cores.
Does anyone have any comment or experience using 45 Deg terminal lugs at 13.8 kv switchgear at the same circumstances. We were intending to get the ZCT replaced with a rectangular one (ABB BYZ-L) which have a 8" x 20" window but the delivery date and procurement process won't make it at this point.
Regards,
We thought of using a UL/CSA Listed 45 Deg-angled terminal block. We got confirmation from our switchgear vendor that the ZCT is fine. I have got our construction folks to measure the clearances using the angled terminal blocks and the clearances are still ok plus the terminations will be covered with additional re-usable insulating boots.
I do not see any issues using the 45 Deg terminals as it matches the natural bend of the cable cores.
Does anyone have any comment or experience using 45 Deg terminal lugs at 13.8 kv switchgear at the same circumstances. We were intending to get the ZCT replaced with a rectangular one (ABB BYZ-L) which have a 8" x 20" window but the delivery date and procurement process won't make it at this point.
Regards,