150KV Line Voltage Drop

Status
Not open for further replies.

eskim

Electrical
May 25, 2003
19
0
0
ID
Dear All,

My friend has problem on 150KV trasmission line about 100km's voltage drop to 120-130KV.

The qustion:
- What is the main cause of this problem usually..all of lead, tower and distance are under rating
- Is there any technic of installing capacitors to correct the voltage drop on HV system..?
- Or is that any corellation between Main step-up transformer that installed at the power plant site..?

Thank you for your kind attention and help.

Regards,
Eskim
 
Replies continue below

Recommended for you

The answer is "it depends". It depends on the system configuration, load, conductor, spacing etc. Is this a radial line? Capacitors can help if the load has low power factor.

Review of a good power engineering text such as Stevenson, "Power Systems Analysis", may be helpful.
 

Power transfer is not specified, but voltage drop is so significant that a voltage/load profile study by an experienced firm would likely have a fast return on investment.
 
Suggestion: The transmission line parameters would have to be reviewed. Sometimes, it is a small cross-sectional area of the conductor, other time it is the transmission line impedance. Shunt capacitors or in-line capacitors may be used. However, the in-line capacitors tend to produce sub harmonics that are detrimental to turbo-generators.
 