wwilson
Electrical
- Sep 30, 2003
- 13
I am in process of designing a machine that requires a 15kVA transformer to accommodate international voltages.
INPUT: DELTA 380/400/415/480 L1-L2-L3, Earth
OUTPUT: 208 L1-L2-L3-N (N bonded to Earth)
The balanced loads will be a 6kw heater (30% duty cycle) and a 1hp blower. The remaining loads are all single phase. I plan to balance the loads as best as possible across the 3 phases.
I can hook up a majority (but not all) of the loads L-L (208 across 2 phases) or L-N (120 single phase) since they are universal voltage switching power supplies. Does anyone see a problem with placing the loads L-L rather than L-N? Especially a problem with the transformer – circulating currents, neutral issues, etc.?
Thanks, wwilson
INPUT: DELTA 380/400/415/480 L1-L2-L3, Earth
OUTPUT: 208 L1-L2-L3-N (N bonded to Earth)
The balanced loads will be a 6kw heater (30% duty cycle) and a 1hp blower. The remaining loads are all single phase. I plan to balance the loads as best as possible across the 3 phases.
I can hook up a majority (but not all) of the loads L-L (208 across 2 phases) or L-N (120 single phase) since they are universal voltage switching power supplies. Does anyone see a problem with placing the loads L-L rather than L-N? Especially a problem with the transformer – circulating currents, neutral issues, etc.?
Thanks, wwilson