Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

1600kW motor Autotransformer start sizing 1

Status
Not open for further replies.

Stefa

Electrical
Sep 18, 2002
7
Could anyone tell me how to size the autotransformer size for starting of 6.0 kV,50Hz,1600 kW induction motor by autotransformer start method.The tap voltage required is 80%,65% and 50% of nominal line voltage.

Thank you
 
Replies continue below

Recommended for you

I would first start with the speed torque curve of the motor and the load. With this calculate the allowable starting time to get the motor+load up to speed. Use the available taps on the auto-transformer to assist you on the starting time and torques available. Please be careful to compensate for the impedance of the transformer.
This should get you started.
 
Are you asking how to design the autotransformer itself? This is normally provided by the motor starter manufacturer based on the motor size.

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor