Hello All,
So we're being asked to prepare a design for a pair of existing windows to be cut wider, from 12"x14" and 24"x33" to 24"x48" each. I've done this type of work a number of times before, but what is bothering me this time is that The interior surface of the wall is heavily salt stained, and the concrete is crumble in your hands weak immediately around the existing windows and for 6 to 8" up the wall to a depth of 1 to 1.5". The wall is 12" thick, and everything else appears to be in good shape. The constructor called immediately upon finding the interior of the foundation wall to be deteriorated, and I have recommended to the client that they undertake to remove and restore all soft areas and follow this by taking steps to waterproof the basement, but this would have to wait for spring.
I'm specifying that the contractor chip down to sound concrete and come back up with Sika 623 as a repair material. The new lintel is being made from jacketing steel, and the compressive strength of the wall is not of significant concern as I am through bolting and having threaded rods epoxied at 450mm centres. In order to allow the wall to now span horizontally, I will have 15M bars at 300mm centres run horizontally across the wall in the Sika 623 and add an outer layer of WWM 6x6-9/9 to control the cracking as the vertical reinforcing. Finally I'll run timber columns at the two ends to not have to rely on the shear capacity of the existing concrete.
The owner wants to press ahead with the work, and says they will correct the deterioration throughout and waterproof or otherwise mitigate the possibility of further deterioration due to water ingress in the spring.
Two questions:
1) I am worried that this current work will get done, everything will be closed up, and the owner will simply not investigate further nor waterproof the foundation. I feel I have a duty of care to see that this is corrected, but at what point does one flag the job to the local authority having jurisdiction? I am certain that water has been involved in the deterioration, but we still don't know what actually caused the deterioration. It almost looks like a freeze thaw damage on a bridge, but goes deeper while being classically moist. Besides, freeze-thaw is not at all likely at the bottom of a heated basement wall! The age of the building does mean that the basement could have been finished laterand the deterioration could have started long ago and been concealed; the fit-up which was demoed in this job was from the 80s and that may have been the first time the basement became occupied space. The contractor advised that the bottom foot of the drywall lining he removed was wet and had mould on the face towards the concrete. The concrete had been covered in a series of 1/4" lath strips to which they fastened the GIB. I'm certain that if we stop the water ingress, we will stop the deterioration, whatever the cause. How far do you push *knowing* the cause of the deterioration, particularly when the damage is still in the cosmetic/poor durability range?
2) Should I insist the whole of the foundation's interior be exposed and subject to repair wherever soft concrete is found? I have already made this recommendation in a field report, but nothing I have seen to date looked to be a structurally compromising situation... It is just heading that way if not addressed.
Your thoughts are appreciated...
So we're being asked to prepare a design for a pair of existing windows to be cut wider, from 12"x14" and 24"x33" to 24"x48" each. I've done this type of work a number of times before, but what is bothering me this time is that The interior surface of the wall is heavily salt stained, and the concrete is crumble in your hands weak immediately around the existing windows and for 6 to 8" up the wall to a depth of 1 to 1.5". The wall is 12" thick, and everything else appears to be in good shape. The constructor called immediately upon finding the interior of the foundation wall to be deteriorated, and I have recommended to the client that they undertake to remove and restore all soft areas and follow this by taking steps to waterproof the basement, but this would have to wait for spring.
I'm specifying that the contractor chip down to sound concrete and come back up with Sika 623 as a repair material. The new lintel is being made from jacketing steel, and the compressive strength of the wall is not of significant concern as I am through bolting and having threaded rods epoxied at 450mm centres. In order to allow the wall to now span horizontally, I will have 15M bars at 300mm centres run horizontally across the wall in the Sika 623 and add an outer layer of WWM 6x6-9/9 to control the cracking as the vertical reinforcing. Finally I'll run timber columns at the two ends to not have to rely on the shear capacity of the existing concrete.
The owner wants to press ahead with the work, and says they will correct the deterioration throughout and waterproof or otherwise mitigate the possibility of further deterioration due to water ingress in the spring.
Two questions:
1) I am worried that this current work will get done, everything will be closed up, and the owner will simply not investigate further nor waterproof the foundation. I feel I have a duty of care to see that this is corrected, but at what point does one flag the job to the local authority having jurisdiction? I am certain that water has been involved in the deterioration, but we still don't know what actually caused the deterioration. It almost looks like a freeze thaw damage on a bridge, but goes deeper while being classically moist. Besides, freeze-thaw is not at all likely at the bottom of a heated basement wall! The age of the building does mean that the basement could have been finished laterand the deterioration could have started long ago and been concealed; the fit-up which was demoed in this job was from the 80s and that may have been the first time the basement became occupied space. The contractor advised that the bottom foot of the drywall lining he removed was wet and had mould on the face towards the concrete. The concrete had been covered in a series of 1/4" lath strips to which they fastened the GIB. I'm certain that if we stop the water ingress, we will stop the deterioration, whatever the cause. How far do you push *knowing* the cause of the deterioration, particularly when the damage is still in the cosmetic/poor durability range?
2) Should I insist the whole of the foundation's interior be exposed and subject to repair wherever soft concrete is found? I have already made this recommendation in a field report, but nothing I have seen to date looked to be a structurally compromising situation... It is just heading that way if not addressed.
Your thoughts are appreciated...