Believe it or not, I am being asked to defend the use of VFDs for a large pumping project where the technology being considered is actually Eddy Current Clutches! I have not run into this idea for years. They currently have them on about 1/2 of their systems, the other half are (our) VFDs. The project scope is going to involve replacing everything because of capacity, so since all of the pumps are going to get bigger, they want to go with new speed control systems that are all the same, no more mixed bag. As you might imagine, the MEs are favoring the Eddy Current Clutch concepts, the EEs are wanting the VFDs. The Eddy Current Clutch people were invited in there yesterday for making a pitch, to which the EE manager was invited. He found himself being on the defensive quite a bit, but he doesn't know Eddy Current Clutches well enough to counter some of the claims they were making, chiefly about how they are easier to fix if something breaks and how they are MORE efficient than VFDs!
Mind you I've heard this before, but it was generally being pitched to EEs who knew better. Now the problem is, the MEs are buying it hook line and sinker and they have the power at the moment because the gist of the project is all about the increased flow. As the mfr of the approved standard of VFDs for this entity, it is falling on me to help my Salesmen retain this as an electrical solution. Here's where I need a little help.
My pitch is fine with regard to MTTR etc. We happen to be the PLC vendor as well, so there is no faster fix to get up and running than swapping out our VFD talking to our PLC, because the PLC stores the entire VFD programming and will automatically reconfigure it when replaced; literally making it plug and play (they are in MCCs). But where I'm struggling is on the energy efficiency issue. I find data from the primary ECC vendors that looks suspiciously like smoke and mirrors to me regarding their efficiencies, plus they appear to be comparing themselves to VFDs using performance data from very OLD studies, maybe even based on old Six Step Inverter technology (they discuss how motor power factor decreases the throughput efficiency of the VFD...). But I also found some independent studies, i.e. Department of Energy funded, where they do not appear to have a bias but are showing that at low flows on centrifugal pumps, the throughput efficiencies of ECC system drops precipitously. Fine, I can use that, especially in that the design flow rates will be 33-69% of pump design capacity at this point; in other words it will ALWAYS be low flow. However, looking at the project description I read that the pumps are almost all Axial Flow and a few Mixed Flow pumps! What I'd like from the experiences of this group is whether I am thinking about this correctly.
I'm not an ME but as I have been told, in an Axial Flow Pump the power requirement actually INCREASES as the flow decreases. I believe in fact that I was schooled (scolded) in here at some point years ago in that the Affinity Laws that make the energy efficiency argument so compelling for VFDs do not really apply to Axial Flow pumps. If that's the case, I may be in trouble. But then again from what I know of ECC drives, they may in fact be in MORE trouble in this case because in order to vary speed, they must increase the slip across the clutch. In doing so, they INCREASE the motor-to-driven-load losses. If the pump then needs MORE power as flow decreases, they are going to have to deliver MORE power at the ery time they have MORE losses. VFD's on the other hand, while not providing the same dramatic Affinity Law savings we are used to, will at lease deliver the REQUIRED power to the motor without added losses. That to me would make a case for VFDs being MORE efficient than ECCs in this application. So even though I may have to counter the initial pitch from our salesmen on the Affinity Law savings, I'd like to be the one who tells them the REAL truth about BOTH concepts.
How does that fly with the collective wisdom of this group?
"Will work for (the memory of) salami"
Mind you I've heard this before, but it was generally being pitched to EEs who knew better. Now the problem is, the MEs are buying it hook line and sinker and they have the power at the moment because the gist of the project is all about the increased flow. As the mfr of the approved standard of VFDs for this entity, it is falling on me to help my Salesmen retain this as an electrical solution. Here's where I need a little help.
My pitch is fine with regard to MTTR etc. We happen to be the PLC vendor as well, so there is no faster fix to get up and running than swapping out our VFD talking to our PLC, because the PLC stores the entire VFD programming and will automatically reconfigure it when replaced; literally making it plug and play (they are in MCCs). But where I'm struggling is on the energy efficiency issue. I find data from the primary ECC vendors that looks suspiciously like smoke and mirrors to me regarding their efficiencies, plus they appear to be comparing themselves to VFDs using performance data from very OLD studies, maybe even based on old Six Step Inverter technology (they discuss how motor power factor decreases the throughput efficiency of the VFD...). But I also found some independent studies, i.e. Department of Energy funded, where they do not appear to have a bias but are showing that at low flows on centrifugal pumps, the throughput efficiencies of ECC system drops precipitously. Fine, I can use that, especially in that the design flow rates will be 33-69% of pump design capacity at this point; in other words it will ALWAYS be low flow. However, looking at the project description I read that the pumps are almost all Axial Flow and a few Mixed Flow pumps! What I'd like from the experiences of this group is whether I am thinking about this correctly.
I'm not an ME but as I have been told, in an Axial Flow Pump the power requirement actually INCREASES as the flow decreases. I believe in fact that I was schooled (scolded) in here at some point years ago in that the Affinity Laws that make the energy efficiency argument so compelling for VFDs do not really apply to Axial Flow pumps. If that's the case, I may be in trouble. But then again from what I know of ECC drives, they may in fact be in MORE trouble in this case because in order to vary speed, they must increase the slip across the clutch. In doing so, they INCREASE the motor-to-driven-load losses. If the pump then needs MORE power as flow decreases, they are going to have to deliver MORE power at the ery time they have MORE losses. VFD's on the other hand, while not providing the same dramatic Affinity Law savings we are used to, will at lease deliver the REQUIRED power to the motor without added losses. That to me would make a case for VFDs being MORE efficient than ECCs in this application. So even though I may have to counter the initial pitch from our salesmen on the Affinity Law savings, I'd like to be the one who tells them the REAL truth about BOTH concepts.
How does that fly with the collective wisdom of this group?