Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations SSS148 on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

1958 Prestressing Strand

Status
Not open for further replies.

pesepeng1

Structural
Apr 13, 2010
3
I am investigating an existing precast, prestressed double tee roof constructed in the late 1950's

I'll be x-raying the members to get strand diameters and locations.

Any ideas as to the likely yield strength of the strands?

I'm guessing 270k strands were not available at the time, and if you look at what the post-tensioning industry was doing around about the same time, they were using button head wires rather than multi-wire strands.
 
Replies continue below

Recommended for you

I'd be pretty careful relying on anything of that era because there were a lot of different manufacturers and not enough standards.

That being said.....ASTM A416 was one of the first (if not THE first) to be a standard for strands. It came about in 1957. It's yield strength (at that time) ranges from 212 ksi (Grade 260) to 230 ksi (Grade 270). AISI 5160 and 9260 bars were used in that era as well. The yield strength there is 130 ksi.

[red]EDIT:[/red] Found this at PCI:

 
And it will be normal relaxation strand, so the relaxation losses will be much higher than we get these days.
 
From the AASHTO Bridge Evaluation Manual

AASHTO_ur4whx.png


I looked at ACI 318-56; it states the Code isn't to be used for prestressed concrete.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor