1A CT to 5A relay input

Status
Not open for further replies.

stevenal

Electrical
Aug 20, 2001
3,798
The preferred low impedance bus differential relay can be ordered with 1A or 5A inputs, but not a combination. The existing breakers have 5A CTs, and the transformer we wish to add has 1A CTs. What problem might occur if I were to run the 1A CT into a 5A input and adjust the ratio in the relay accordingly? Should I use auxiliary CTs to drop all the 5A CTs to 1A and order the 1A version of the relay? Thanks. Merry Christmas
 
Replies continue below

Recommended for you

I would think that if you just put in the correct CTR all should be fine. You'll lose low-end accuracy (measurements potentially lost in the weeds) but shouldn't confuse the relay during faults. I wouldn't go the other direction though, connecting a 5A CT to a 1A input could cause trouble in that the relay A/D will "saturate" at 20% of the current it would with a 5A input.

Is the transformer a possible source or is it just a load?

I’ll see your silver lining and raise you two black clouds. - Protection Operations
 
David,

Thanks. We tend to treat the transformer as a source and trip the circuit switcher in case of a bus fault. In reality, it feeds radially. Normally open switches parallel substations only long enough to complete a load transfer, so the chance of a bus fault occurring during such a transfer is very low.
 
That means that the CT will perform satisfactorily for any bus fault. Then you just need to be concerned about its performance for a transformer fault. But that's a concern regardless of the secondary current.

I’ll see your silver lining and raise you two black clouds. - Protection Operations
 
If I remember right, the CT secondary amps is settable for each CT individually in modern numerical relays.
I mean the relay analog input is suitable for connecting either 1A or 5A secondary CTs and the selection is part off the relay setting configuration. Just checkout.
 
Some relays (SEL) determine the Inom sec at the time of ordering. Others (GE, etc) have dual inputs.
 