Hello ALL,
we install new (1Mw 3.3Kv motor DOL) connected to 3.3kv BB when when we try to switch it on. Sometimes especially after long motor shutdown it cause generator differential relay to Pickup and trip the generator. The 87G should be stable even if the mortar draw high stating current.
but after one or two attempt starts of the motor its working ok.
we have same old motors (rating and manufacturer) that working in the plant does not cause this problem
Generator differential relay is BASLER BE1-87G (its pickup 100amp primary). we carry out secondary injection of the relay and its working fine.
Thanks in advance.