Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations GregLocock on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

20 amp recepticles on 25 amp breaker

Status
Not open for further replies.

ThinkingARB

Mechanical
Oct 25, 2007
2
I have a requirement to place plug-in 1.08 kW, (115v) hotplates throughout a resturant. The challenge is to avoid adding another electrical panel and more breakers I hoping to place two plug-in hotplates on there own single, 120v/20 amp receptacle with those two single recepticles connected on the same 25 amp breaker.

So the question is can a 20 amp receptacle be placed on a 25 amp overcurrent protected circuit?
 
Replies continue below

Recommended for you

Not the correct forum, but...

Absolutely not... no more than you could use an undersized wire on such a circuit.


Dan - Owner
Footwell%20Animation%20Tiny.gif
 
Not legally in either the US or Canada.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor