Hi,
I've been waiting to write this for 8 months just to proof that the engine is OK.
About 8 months ago we have an incident that generator breaker was fail to open, resulting approx about 20 minutes we have reverse power about -1 MW. At that time the operator donot realize that breaker fail to open so they shut the fuel valve. After calling one of the Senior operator he found out that breaker fail to open and he open the "downstream" breaker in swicth yard to shut the electricity to the plant.
We change the failed breaker, check every part of diesel engine closely, Nothing found damage. I think one of the mech eng do NDT test to find cracks. No cracks. coupling in good condition.
Test the engien full load for several hours, OK.
The engine is 5 MW, and 6 years old.
The reverse power protection for genset is set at 5% 10 seconds delay. (recommended by genset mfr)
During the investigation meeting one of analogy come up from one of mech eng, that motoring the diesel engine is same as if you riding your truck down hill and put to low gear and let the engine to do the breaking job.
The question
Is any one experince prolong motoring on diesel engine cause engine to cath fire or explode (as per IEEE buff book) ?
Now we change the delay to 30 secs to avoid reverse power trips since the diesel engine we use to chase erratic load, and steam plant as base load.
I've been waiting to write this for 8 months just to proof that the engine is OK.
About 8 months ago we have an incident that generator breaker was fail to open, resulting approx about 20 minutes we have reverse power about -1 MW. At that time the operator donot realize that breaker fail to open so they shut the fuel valve. After calling one of the Senior operator he found out that breaker fail to open and he open the "downstream" breaker in swicth yard to shut the electricity to the plant.
We change the failed breaker, check every part of diesel engine closely, Nothing found damage. I think one of the mech eng do NDT test to find cracks. No cracks. coupling in good condition.
Test the engien full load for several hours, OK.
The engine is 5 MW, and 6 years old.
The reverse power protection for genset is set at 5% 10 seconds delay. (recommended by genset mfr)
During the investigation meeting one of analogy come up from one of mech eng, that motoring the diesel engine is same as if you riding your truck down hill and put to low gear and let the engine to do the breaking job.
The question
Is any one experince prolong motoring on diesel engine cause engine to cath fire or explode (as per IEEE buff book) ?
Now we change the delay to 30 secs to avoid reverse power trips since the diesel engine we use to chase erratic load, and steam plant as base load.