20 psf minimum roof live load

PE_JRM

Civil/Environmental
Mar 20, 2024
44
This a pretty basic question so please forgive me for asking but my area of expertise doesn't include buildings. I am renovating an old building that I own and I would like to check what the contractor proposes for the roof system and its effect on the rest of the structure against code requirements.

I understand that the 20 psf minimum roof load is intended to account for future roof maintenance. In my case I believe the minimum can be reduced from 20 psf to 12 psf according to the code. The code says the minimum roof LL is not required to be applied concurrently. If we design for a 20 psf live load on the roof the foundation must be adequate to carry that load. The foundation must carry roof and floor loads and designing for max roof LL and max floor LL at the same time makes no sense. But designing the roof structure for 20 psf LL and ignoring those effects below the roof also makes less sense ("need not be applied concurrently").

With regard to foundation checks what makes sense to me is some percentage of max floor LL combined with the the loads from the roof. I don't see that anywhere in the code required load combinations. Please help me understand what the code requires.

Background info: I live in a region where snow and ice are pretty rare so the required snow load is 5 psf. The roof DL is only 6 psf (corrugated steel on osb deck with steel Zee purlins 24" OC spanning 20 ft). The foundation in my old building is marginal and showing it "good" is difficult with the 20 psf minimum roof LL requirement. The building is also in an area where code enforcement was non-existant 50 years ago.
 
Replies continue below

Recommended for you

Live load reduction is not for the entire roof. It's for certain members that make up the roof structure. So your purlins will need to be designed for 20psf. The girders might be able to be reduced to 12psf. Maybe.

As for applying full roof and floor live loads at the same time, you're right. It doesn't make sense. Which is why the code doesn't require it.

If building structures are not your area of expertise, you should get a structural engineer involved to do the design.
 
Thanks phamENG. I am a structural engineer but I've never done a building. There ARE other sorts of structures you know. I've done a wide variety of structures and worked with at least half a dozen codes and Federal regulations in my 40+ year career as a Professional Engineer. Never a building, Zero experience with UBC. I own this building and it is outside any code jurisdiction so I can do whatever I want with it. I'm just looking for a rational criteria to judge the foundation capability before I start modifying the structure.

Perhaps you should let someone else answer the question if you cant answer without insulting the questioner.
 
There ARE other sorts of structures you know.
Yep. I am aware of that.

Which is why when somebody calls me to design a bridge for them, or an MSE retaining wall, or a vent stack, or a silo, or one of any number of structures in which I lack the experience and the knowledge to provide adequate engineering services, I turn down the job and, if I can, refer to them to somebody more suited for it. It's also why I hire other engineers to practice their specialties at my property. I'd rather have it done right. I may ask them questions to learn, but I let them do their job.

I'm simply suggesting you do the same.
 
Engineers are not often involved in residential very small building construction. This building is the size of a big garage or workshop. Like I said, I'm doing a sanity check on the contractors proposal. Its not worth the cost spent to me to hire an expert when its not even necessary/required to do the checks. I'm trying to determine if there is enough load applied to the edges of a 4" slab to crack it using recommended design loads and combinations. The contractor says its fine based on his experience. I'm checking up on him - I'm not so sure.

HUD residential construction guidelines (a table footnote) tell me that the 20 psf minimum roof load DOES NOT have to be combined with any other transient loads. ASCE and UBC have similar requirement . I believe the rational is that the roof structure needs be adequate to support temporary construction loads. The reason for the requirement makes sense. But the reason that temporary construction load doesn't have to be combined with a percentage of other live loads does not make sense to me. There is always some live load on a floor. It is never ZERO. Thus, my "confusion" and desire to understand the why of things instead of because the code requires it.

BTW, this roof structure is longitudinal purlins supported by interior walls. No rafters or girders.
 
Not sure UBC is even used anymore. IBC is the generally accepted code in most of the US.

The IBC (which references ASCE 7) has load combinations where floor live and roof live do add together - but at a reduced value due to the small statistical nature of both loads occurring simultaneously. For ASD it's 0.75L + 0.75Lr. For LRFD it's 1.6L + 0.5Lr and also 1.0L + 1.6Lr.

I agree with all phamENG said above and if answers here don't satisfy suggest, for your head check, that you hire a local structural engineer to at least take a quick look at your project - an hour's time for a head check perhaps.

I didn't see anything pham said that was an insult. It's free advice - take it or not - your choice.
 
Not sure UBC is even used anymore. IBC is the generally accepted code in most of the US.

The IBC (which references ASCE 7) has load combinations where floor live and roof live do add together - but at a reduced value due to the small statistical nature of both loads occurring simultaneously. For ASD it's 0.75L + 0.75Lr. For LRFD it's 1.6L + 0.5Lr and also 1.0L + 1.6Lr.

I agree with all phamENG said above and if answers here don't satisfy suggest, for your head check, that you hire a local structural engineer to at least take a quick look at your project - an hour's time for a head check perhaps.

I didn't see anything pham said that was an insult. It's free advice - take it or not - your choice.
Thanks for the ASCE code reference. I'll check it out.
 
I'm real confused how a structural engineer who has practiced for 40+ years is unfamiliar with load combinations? PE_JRM, what kind of projects do you typically work on?
 