It's a screw auger type of pneumatic pump used for Portland cement (dry powder) transfer. Amp draw should be roughly linear with load increase.
compman72,
I think aolalde has a very good point, but if you don't understand what he meant I'll give you the brief rundown.
Many large motors are designed for what is called Y-Delta starting, a way of reducing the starting torque and current on startup by using a 2 step process. In the fist step, the motor windings are connected in a Wye (Star) pattern, which provides only 33% of the torque but also reduces the starting current to 33% or normal. Then after the motor is nearly at full speed, the winding pattern is switched to Delta which provides full torque.
Y-Delta starting is very problematic and a lot of people choose instead to use solid state starters such as the Benshaw unit. The problem aolalde mentioned would be that at some time in the past when someone swapped out the Y-Delta starter, they mistakenly connected the motor to the Benshaw starter in the Y pattern instead of Delta. So all along, you probably have been operating that motor in the reduced torque mode, i.e. 33% of full capacity. That has apparently been fine up until now because your flow demand has been low so nobody noticed, but as you now try to increase flow, the motor torque is so low that you are stalling it almost immediately.
The numbers add up to point to this problem as well. If you were stalling a 200HP motor properly connected (in Delta), the Locked Rotor Amps could go as high as 1440A. If however as you say, it is going to +400A, guess what? 1440 x 33% (Wye connected Locked Rotor Amps) = 475A!
Have a qualified motor shop or an electrician familiar with Y-Delta motors take a look at the motor connections.