I been designing s1 warehouse for a long time and i have an s1 warehouse with fully sprinklered efsr system installed in this new building
Is a fire alarm system.required
I say 100 percent not required but have a fire code offical.that say it required
Any input would be great
907.2
If it not listed by classifsction it not required
S
1. Ask the nice plan reviewer for the section they are referencing to require.
2. Ask same nice person, is there a local amendment that covers it
3. Ask same nice person, do they mean monitoring only, and not all bells and whistles
901.6 Supervisory Service
Where required, fire protection systems shall be monitored by an approved supervising station in accordance with NFPA 72.
901.6.1 Automatic Sprinkler Systems
Automatic sprinkler systems shall be monitored by an approved supervising station.
Besides the 901.6 Supervisory Service referenced some states (Georgia is one of them) require central station alarms on everything 20 heads an up.
The
System is fully montired and all.flows.and.tampers.are electrically connencted
All i m.looking for is there anyware i might have missed that states a fire alarm system is required in S1
Inspector is stateing sec 907.2 through 907.2 .23 requires S1 to have notifaction in warehouse ie horn and strobes
The above sections list all requirements for.all types of use group but does not list
S 1 or s2 so therefour it not required
1. Set down with inspector and book and ask him to point to where he says, the system is required
2. Or talk to his boss and ask boss where it is required
3. Should not matter, are you doing high piled stock,,,,or Big ass fans??
4. Local amendment ????
Two hvls fan with shutdown
And typical.rack.storage
No local.addmendments
The guy is dead wrong anda.will.not back.Down
And.owner wants.co
Check with the insurance carrier as to what they want since the owner will pay more premium for the life of the building. You may win the argument with the local officials but pay more insurance cost for property, liability and umbrella insurance coverage.
Keep going up the food chain, till you find intelligent life,
So there was no up front plan review,,
With the fire alarm requirement as a comment??
Have approved plans.from township and.this guys says it does not matter
I he can fai or change anything upon inspection
I would say yes, if something seen different at final inspection, than on plans.
Which inspector is this building or fire or other?
Do they have a boss,