Well, maybe, "Alright- I can tell folks here have never seen a need for 1000kw of backup power at 120/208 so I will include an example of where a 600kw and 400kw unit was used to meet the need:"
Frankly your design isn't all that unique, worked in lots of facilities that had multiple generators supplying groups of ATS switches and other loads. If the loads aren't critical then that system may be ok, but you have no redundancy. I recently worked on a system that started out like what you have drawn, and then was modified to add additional ATS switches to try and cross connect certain circuits, got to be a bit of a nightmare. Because of some seismic issues the whole facility is going to get a major rework with a completely new power system that will be based on an N+2 "Power Block" generator system with a mixed bag of diesel and natural gas units.
Not sure how old you are or where in the world you work, but this was a fairly common issue for the generator suppliers in the late 80's up until around Y2K. Older healthcare facilities trying to grow without making massive changes to their infrastructure, telecom facilities shifting from analog phone lines to digital with increasing power needs, and growth of older data centers that started with 120/208 systems and kept trying to grow them without huge changes.
You may also live in an area where things like runtime limits and strict air quality regulations don't have an impact on your design criteria, but they may.
One of the primary reasons companies like CAT and other generator set suppliers don't make bigger 120/208 sets is that with better control and protection systems now available a lot of emergency systems are going to smaller multiple generators for various reasons.
Take a typical healthcare facility in my state, following OSHPD guidelines for sizing you end up with a generator that is usually way oversized from actual connected loads, but you may need that capacity for energizing transformers, starting motors and recharging UPS systems. Then after a short time your big generator is running at loads well below its rating. With older design engines it wasn't really much of a problem, but newer high output lower emissions engines with lots of turbocharging don't do too well running at lower loads, if you have to deal with exhaust after-treatment systems it really gets difficult.
A large number of the systems I work on these days use multiple units, when an outage occurs, they all start and come online, power system gets restored, then as everything stabilizes and loads level out, the control system using a load demand strategy takes excess capacity off line.
You may find this an interesting read, not the only company that does it, but one of the better technical descriptions I have found,
Another company with a lot of nice sales type info but not a lot of technical detail is this,
But have been seeing a fair number of systems by them landing in our area in the last couple years.
To answer another of your questions, yes, most manufacturers will provide a non-standard tail end, but the one off structural and torsional engineering will likely make the cost way higher than the standard packages. There may also be some certifications involved depending on where this will land, so those costs will factor in as well. Some genset dealers excel in providing custom engineered packages, but again cost will be higher that a standard model, and hard to get someone to pay the extra money unless you're dealing with an industry that is used to paying more for exactly what they want. In my experience standby system for government and healthcare are almost always driven to the lowest bidder.
Hope that helps, MikeL