Hopefully someone can help me understand the following:
We have a UPS that was installed in the 80's. The input is from the A and B phase of a 3 phase 480/208 delta/star transformer at 208VAC. The UPS has an internal output isolation transformer on it. The plant take the A phase to neutral (120VAC)from the input and put it through a make before break external bypass switch. They also only use the A phase to neutral (120VAC) on the UPS output which also goes to the bypass switch.
I have always understood that you cannot use a normal 208VAC single phase in and out UPS with a make before break bypass switch. This is confirmed at this site as there is a 60VAC difference between the A phase input and the A phase output on this UPS while on static bypass.
What I don't quite understand is why the phase differnce is there. I have always thought that there is no noticable phase shift on the primary and secondary of a single phase isolation transformer. I realize that the input to this transformer is 2 phases of a 3 phase 208VAC supply but the potential across the primary winding is still 208VAC single phase. Therefore I would have thought that the secondary 208VAC would be in phase with the input. Why is this not the case?
I understand that the 120VAC will be out of phase because they are artificially created by winding taps on the secondary of the transformer rather than the A phase and B phase being 120 degrees apart and the neutral being created by a star center point.
I also understand that the fix to this situation is to install a 208VAc to 240VAC transformer on the input and install a 240VAC to 240VAC UPS. This will allow the use of an external make before break bypass switch.
Could someone help me understand the 208 to 208 phase shift?
UPS Service Manager
We have a UPS that was installed in the 80's. The input is from the A and B phase of a 3 phase 480/208 delta/star transformer at 208VAC. The UPS has an internal output isolation transformer on it. The plant take the A phase to neutral (120VAC)from the input and put it through a make before break external bypass switch. They also only use the A phase to neutral (120VAC) on the UPS output which also goes to the bypass switch.
I have always understood that you cannot use a normal 208VAC single phase in and out UPS with a make before break bypass switch. This is confirmed at this site as there is a 60VAC difference between the A phase input and the A phase output on this UPS while on static bypass.
What I don't quite understand is why the phase differnce is there. I have always thought that there is no noticable phase shift on the primary and secondary of a single phase isolation transformer. I realize that the input to this transformer is 2 phases of a 3 phase 208VAC supply but the potential across the primary winding is still 208VAC single phase. Therefore I would have thought that the secondary 208VAC would be in phase with the input. Why is this not the case?
I understand that the 120VAC will be out of phase because they are artificially created by winding taps on the secondary of the transformer rather than the A phase and B phase being 120 degrees apart and the neutral being created by a star center point.
I also understand that the fix to this situation is to install a 208VAc to 240VAC transformer on the input and install a 240VAC to 240VAC UPS. This will allow the use of an external make before break bypass switch.
Could someone help me understand the 208 to 208 phase shift?
UPS Service Manager