I have a fairly large building that is currently wired all with 208V, because the wiring was done probably int he 1950s. If it were being wired today, it would certainly use 480v distribution. THe building is 500,000 sq ft on 4 floors, and several of the floors have 20' cielings. That doesn't count the dome on top, which lofts into the air high enough it needs an airplane landing light.
We are charged with installing a new emergency riser (optional standby system to supply computers and IT equipment) throughout the building. I am concerned that at 208V, we will be strapped with voltage drop problems when we get to the other end of the building.
Currently the voltages in the building are 4160 and 208. 4160 is scheduled to vanish the next time the building is renovated.
Maintenance staff is very sophisticated, they have no problem with higher voltages and 480 or even medium voltage switchgear. The building is a State Capitol, it is going to be continually renovated generation after generatio as things become obsolete.
My question is, in your opinion would it be foolish to introduce 480V into this building, where it never was before, or, ont he other hand, would it be wise to look forward and install a more modern distribution system?
We are charged with installing a new emergency riser (optional standby system to supply computers and IT equipment) throughout the building. I am concerned that at 208V, we will be strapped with voltage drop problems when we get to the other end of the building.
Currently the voltages in the building are 4160 and 208. 4160 is scheduled to vanish the next time the building is renovated.
Maintenance staff is very sophisticated, they have no problem with higher voltages and 480 or even medium voltage switchgear. The building is a State Capitol, it is going to be continually renovated generation after generatio as things become obsolete.
My question is, in your opinion would it be foolish to introduce 480V into this building, where it never was before, or, ont he other hand, would it be wise to look forward and install a more modern distribution system?