Selfentitled
Electrical
- Feb 28, 2005
- 8
This question has been bothering me for a while..
There are a lot of products on the market that can be connected using a 208V, single phase connection (two phases and one ground).
Where does the unbalanced load go? If I connect this equipment to two phases of a 120/208V panel (120 degree shift between phases), I should have an unbalanced load, and this load should return on the neutral wire. But there is no neutral wire, so where does the unbalanced load go?
If this equipment draws 20A at 0 degs on the A phase, and 20A at 120 degs on the B phase, then I should expect to have 20A at -120 degs on the neutral.. Luckily I don't have to worry about the 20A of unbalanced current on the neutral because the neutral isn't connected.
Any expert insight would be much appreciated! Thanks!!