220 kV Cable Straight Length GIS Termination

Status
Not open for further replies.
Replies continue below

Recommended for you

IMO the actual straight length of the cable is stated by termination manufacturer, as a part of accessories is connected with. For instance, on the attached sketch of Raychem 145 kV termination the C dimension includes gland and sealing part. I think the dimensions correspond to IEEE 1300 or IEC 60859 [which a have not with me].

 
 http://files.engineering.com/getfile.aspx?folder=194f4a1f-7f28-4621-947c-2ad2badd965a&file=Raychem_145_kV_termination.jpg