Simple question.
I'm building a control panel for a powder coating oven. It will have 3 3,000 watt 220 volt heating elements. On the Oven building forums they seem to only put over current protection on one leg of the 220 feeding the elements. I am under the impression that...
The relay that powers the elements should be 2 pole.
Both legs of power should be protected (fuse or breaker) via a 2 pole breaker.
I am running 50 amp to a 2 pole, SS relay to power the 3 elements. I am running 3 circuits from the relay to 3 2 pole, 20 amp breakers and 14ga wire from the breakers to each element.
The group is telling me this is overkill and one fuse on the 220 to a single pole relay would be fine.
This will leave one leg hot all the time, and I believe it leaves one leg unprotected. Also this would require the wire to the elements to be sized for the full 50 amps Correct?
All of my background is in three phase controls and we wouldn't think of doing it any other way.
I hope it wasn't too confusing.
I'm building a control panel for a powder coating oven. It will have 3 3,000 watt 220 volt heating elements. On the Oven building forums they seem to only put over current protection on one leg of the 220 feeding the elements. I am under the impression that...
The relay that powers the elements should be 2 pole.
Both legs of power should be protected (fuse or breaker) via a 2 pole breaker.
I am running 50 amp to a 2 pole, SS relay to power the 3 elements. I am running 3 circuits from the relay to 3 2 pole, 20 amp breakers and 14ga wire from the breakers to each element.
The group is telling me this is overkill and one fuse on the 220 to a single pole relay would be fine.
This will leave one leg hot all the time, and I believe it leaves one leg unprotected. Also this would require the wire to the elements to be sized for the full 50 amps Correct?
All of my background is in three phase controls and we wouldn't think of doing it any other way.
I hope it wasn't too confusing.