snclap2
Electrical
- Aug 21, 2002
- 1
I am retrofitting the high voltage bus at an existing substation. I am upgrading the bus from 2000 amp 40 kA to 3000 amp 63 kA by increasing the schedule from 4 inch schedule 40 to 4 inch schedule 80 extra high strength with the upgraded station post type insulators. The structural engineer believes that there will be no structural forces at the support structure that he will have to worry about. I have told him that the standards show that the force from the increased short circuit will apply to the structure at the support point of the insulators. He believes that the forces will cancel out. I believe we need a new heavier or stronger structure. Can anybody give me an idea who is correct on this one?
Steve
Steve