24 VAC

Status
Not open for further replies.

dougjl

Electrical
Sep 14, 2001
44
I have a question about running some control wiring. I will have an 120 VAC cable tray and a 24 VDC cable tray running between my controller and field devices. I have one field device that will require 24 VAC. Should I run this cabling in the low voltage DC tray or the 120 VAC tray? I am not sure where this voltage should sit and if the AC nature of it would adversely affect the DC wiring.

What do ya'll think?

Thanks,
Doug
 
Replies continue below

Recommended for you

I don't know what the code says, but if the 24VAC is low power (assume so since controls) then running it in with DC will not hurt a thing. The issue with running AC with DC (at least in my opinion) is the potential for EMI problems. EMI is not a problem if it all wires in the raceway are low current carrying and are not hooked to fast switching devices.
 