Is an AC overpotential test common for air insulated 230 kV substation commissioning?
A utility's spec calls for "AC Hi-pot Test of Circuit Breaker and Applicable Bus Sections" in a checklist attachment to their generic circuit breaker installation specification that is used for breakers from 5 KV-500 kV. The AC test voltages are not specified, so the utility engineer requested we replicate the circuit breaker factory test (425 kV AC for 3 minutes). Field tests are usually 75% of factory tests= 75% x 425 kV = 319kV AC.
I haven't been able to locate a 300kV + AC hypot.
The utility's substation maintenance staff doesn't recall doing any AC overpotential test other than Doble power factor insulation tests at 10 kV.
Our normal 230 kV field testing protocol is a full set of Doble power factor tests at 10 kV AC and a DC insulation resistance test plus any manufacturer required or recommended tests. The breaker manufacturer does not list any overpotential tests in their O&M manual.
The >100kV test equipment I've seen are variable frequency resonant units that come on two semi-truck trailers and require a minimum circuit capacitance to build the voltage. A breaker with 8 feet of bare cable on either side is not much cpacitance, I don't think we could get that style to work.
If AC overpotential testing is common, I would have expected there to be more than a handful of "portable" AC High Pot test sets in North America.
Thanks in advance for any feedback.
A utility's spec calls for "AC Hi-pot Test of Circuit Breaker and Applicable Bus Sections" in a checklist attachment to their generic circuit breaker installation specification that is used for breakers from 5 KV-500 kV. The AC test voltages are not specified, so the utility engineer requested we replicate the circuit breaker factory test (425 kV AC for 3 minutes). Field tests are usually 75% of factory tests= 75% x 425 kV = 319kV AC.
I haven't been able to locate a 300kV + AC hypot.
The utility's substation maintenance staff doesn't recall doing any AC overpotential test other than Doble power factor insulation tests at 10 kV.
Our normal 230 kV field testing protocol is a full set of Doble power factor tests at 10 kV AC and a DC insulation resistance test plus any manufacturer required or recommended tests. The breaker manufacturer does not list any overpotential tests in their O&M manual.
The >100kV test equipment I've seen are variable frequency resonant units that come on two semi-truck trailers and require a minimum circuit capacitance to build the voltage. A breaker with 8 feet of bare cable on either side is not much cpacitance, I don't think we could get that style to work.
If AC overpotential testing is common, I would have expected there to be more than a handful of "portable" AC High Pot test sets in North America.
Thanks in advance for any feedback.