I'm having trouble finding the ampere ratings for a 250 HP 480V, 3-Phase motor.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
In general the NEC says that the motor currents shown in Tables 430.247, 430.248, 430.249, and 430.250 shall be used to determine the ampacity of conductors or ampere ratings of switches, branch-circuit short-circuit and ground-fault protection, instead of the actual current rating marked on the motor nameplate. 430.6(A)(1)If you do, you should only use the motor nameplate information.