I have a difference of opinion that i am hoping people on here can help me weigh in on. we have a switchgear with 5 cells. only 2 of the cells have breakers and are being used (incomer and line 1). The client wants to run CT cables from the switchgear building (tappered off and shorted at the switchgear building's MRs) all the way to the bus protection in the main building. The problem arises when shortening and grounding these cables.
The Relay (MFAC34)'s sumation will ideally have all of the CT cables connected but if we ground and short, would this not cause the relay to not function properly as any fault on the other relays would simply flow back through the ground on these spare cables?
After talking with an acceptor, one proposed idea would be fully wiring out and connecting the spare cells bus prot CT’s to the summation module.
Otherwise the summation module would have to be isolated from wiring in order to no add in the extra short or grounds into it.
suggestions?
I have a difference of opinion that i am hoping people on here can help me weigh in on. we have a switchgear with 5 cells. only 2 of the cells have breakers and are being used (incomer and line 1). The client wants to run CT cables from the switchgear building (tappered off and shorted at the switchgear building's MRs) all the way to the bus protection in the main building. The problem arises when shortening and grounding these cables.
The Relay (MFAC34)'s sumation will ideally have all of the CT cables connected but if we ground and short, would this not cause the relay to not function properly as any fault on the other relays would simply flow back through the ground on these spare cables?
After talking with an acceptor, one proposed idea would be fully wiring out and connecting the spare cells bus prot CT’s to the summation module.
Otherwise the summation module would have to be isolated from wiring in order to no add in the extra short or grounds into it.
suggestions?