I am adding a switchgear with 4 25kV feeder breakers and Transformer. The existing 25kV Bus had 4 feeder breakers. We are using one of the breakers as a Tie to connect to the new addition.
my question is:
1. there's an existing U/F relay for the feeder breakers, but i am not sure if the TIE would require to be connected to the U/F relay, this TIE is N.O.
Client says U/F is for feeders themselves usually so he is saying no to connecting the tie. Is this correct? and why? wouldn't you want to protect the TIE either way? It does look like the TIE will never be N.C.
Follow up question, would my new feeder breakers have to be tripped by this existing U/F prot? or would we need a new one?
2.- About TX protection; do I need a 50NN function on my relay for a NGR? or is this only when it is high impedance?
Silly follow up question, how do i know if the NGR is high impedance? I don't actually have a lot of documentation on the NGR other than it is dry-type air core NGR 150A continuous current for 27.5kV.
I would appreciate some input.
Thanks
my question is:
1. there's an existing U/F relay for the feeder breakers, but i am not sure if the TIE would require to be connected to the U/F relay, this TIE is N.O.
Client says U/F is for feeders themselves usually so he is saying no to connecting the tie. Is this correct? and why? wouldn't you want to protect the TIE either way? It does look like the TIE will never be N.C.
Follow up question, would my new feeder breakers have to be tripped by this existing U/F prot? or would we need a new one?
2.- About TX protection; do I need a 50NN function on my relay for a NGR? or is this only when it is high impedance?
Silly follow up question, how do i know if the NGR is high impedance? I don't actually have a lot of documentation on the NGR other than it is dry-type air core NGR 150A continuous current for 27.5kV.
I would appreciate some input.
Thanks