Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations The Obturator on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

25kV VT Ground alarm

Status
Not open for further replies.

Sn00ze

Electrical
Jan 16, 2013
176
Hello everyone,

I was going through some old projects and I noticed that in some of them, a VT Ground alarm is used for a 3-ph single winding PT (120V) used for metering. I remember the project engineer said that they don't normally use a Gnd Alarm for 25kV VT's unless there are special considerations.

I have another project now where the project engineer is saying to go ahead and get a Gnd Alarm for a very similar project. That is, a 25kV bus VT

Does anyone have any standard or rule I can refer to? or personal experience as to this preference? What special conditions should i consider in order to justify a Gnd alarm?

I appreciate any insight. thanks!

 
Replies continue below

Recommended for you

Thank you 7anoter4, i'll have some good reading material over the weekend :)
 
Hi Snooze,
Is the 25kV system solidly grounded? Can you provide a [very] simple 1-line diagram?
I have used [once] a type 64 relay before to detect grounds on a 25kV solidly grounded incoming Utility feeder. The PT configuration was grounded-wye / broken delta, with the 64 relay across the broken-delta secondary. This relay was used to detect ground-faults on the incoming Utility supply and trip the incoming circuit-breaker. The Customer in this case has a whole bunch of grid converted 4-quadrant inverters and routinely would export power back to the Utility. The Utility was concerned wrt the Customer backfeeding into a ground on the Utility side. Note: the Customer's step-down transformers were delta-wye.


The pessimist sees difficulty in every opportunity. The optimist sees the opportunity in every difficulty.
Winston Churchill

 
Hello GroovyGuy,

Here's a rough single line sketch. VT taps off of the 25kV Bus directly.
vt_n7rfik.jpg


and yeah it is solidly grounded.
 
Hey Snooze,
You have a 25kV solidly grounded system, and you wish to install a 'ground alarm' relay.

I trust that you also have some form of (current-based) ground detection on the system as well. Either residually connected CTs and a 50N/51N relay, or zero sequence CTs and a 50G/51G relay. Of course, I have assumed that your system uses 25kV CBs and not HV fuses for O/C protection, but perhaps this is not the case? I understand that you work in the Utility (substation) side of the business, so I suspect that you will be using SEL multi-function relays for feeder protection (on CBs), n'est pas?

In my limited experience, in industrial power systems, a MV system (ie 25kV) either has a ground-fault, or it does not. There is no middle ground, at least on (shortish) feeders. Of course longer feeders, transformers and motors can be more of a challenge. I take it this is why you are considering a ground-alarm relay on the system.
GG


The pessimist sees difficulty in every opportunity. The optimist sees the opportunity in every difficulty.
Winston Churchill

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor