We are installing 480/277 3phase in our building. I want to install 277V lighting fixtures that use 1.9A @ 277V. Is the following logic correct?:
1) I should try to balance the current in the circuit by running equal numbers of lights on each leg.
2) wiring three fixures on each line to neutral results in 5.7A on each line, and a 3 bus breaker should be sized according to this current. They can share the same neutral wire.
3) the neutral wire needs to be sized accordingly to provide sufficient return path. According to Section 220.22, the neutral demand load shall be “the maximum unbalance computed load between the neutral and any one ungrounded conductor.” So I size that at 5.7A as well?
4) Doubling the unbalanced current is good practice, so it should actually be sized at 12A
Just want to make sure I am not missing something with respect to circuit sizing. I also see 480V ballasts are available and less common. I can see why the 277's are more popular if my assumptions above are correct.