I have an upcoming project where the second floor will be used to store cars. It is not a parking garage in the sense that cars will be coming and going daily. It will be covered with a roof and enclosed with CMU walls. Think of it as a second story car showroom. I plan on asking what the heaviest vehicle to be stored up there will be but for now lets assume average passenger cars.
ASCE 7-02 states that the minimum live loads are 40 psf or a 3000lb point load over a 4.5 in x 4.5 in area. 40 psf seems light in comparison to other typical floor live loads. The commentary seeks to explain this by stating that load variation is very small in parking garages versus buildings. Still even with live load reductions most building areas would be designed for more load than this.
I plan on taking the heaviest car and dividing by its area to make sure the 40 psf load is adequate. I will also probably go ahead and design for a live load of 100 psf since the minimum corridor load is 100 psf. Doesn't make much sense to design corridors for more load than a floor holding up cars. I doubt the cars will be packed in close together since it will be used for private use. Also since this space may be used for something else in the future (many owners will assume it can take a lot since it was used for cars) I think 80 to 100 psf may be appropriate.
I'm thinking of using either composite steel beams or LH series steel joist with a heavy concrete poured form deck. I won't be using a composite deck since I'm worried about the effect the concentrated wheel loads might have on the interlocking action over time. I'm a bit concerned since most parking garages use concrete exclusively. My thought however is that if the concrete deck can handle the load concentration then steel beams and CMU walls should be fine. Of course the joist or beams must also be capable of handeling the concentrated loads as well.
Does anyone have anything else to add or am I pretty much on the right track here? Is there anything else I should consider in my design?
Any help from you parking garage engineers will be much appreciated.
Thanks,
John
ASCE 7-02 states that the minimum live loads are 40 psf or a 3000lb point load over a 4.5 in x 4.5 in area. 40 psf seems light in comparison to other typical floor live loads. The commentary seeks to explain this by stating that load variation is very small in parking garages versus buildings. Still even with live load reductions most building areas would be designed for more load than this.
I plan on taking the heaviest car and dividing by its area to make sure the 40 psf load is adequate. I will also probably go ahead and design for a live load of 100 psf since the minimum corridor load is 100 psf. Doesn't make much sense to design corridors for more load than a floor holding up cars. I doubt the cars will be packed in close together since it will be used for private use. Also since this space may be used for something else in the future (many owners will assume it can take a lot since it was used for cars) I think 80 to 100 psf may be appropriate.
I'm thinking of using either composite steel beams or LH series steel joist with a heavy concrete poured form deck. I won't be using a composite deck since I'm worried about the effect the concentrated wheel loads might have on the interlocking action over time. I'm a bit concerned since most parking garages use concrete exclusively. My thought however is that if the concrete deck can handle the load concentration then steel beams and CMU walls should be fine. Of course the joist or beams must also be capable of handeling the concentrated loads as well.
Does anyone have anything else to add or am I pretty much on the right track here? Is there anything else I should consider in my design?
Any help from you parking garage engineers will be much appreciated.
Thanks,
John