ctcray
Structural
- Jan 23, 2006
- 90
Situation: 2x12 SPF #2 Ledger fastened to concrete wall with 3/4" bolt @ 12"oc at the centerline of the ledger, supporting 336 plf total load. From 2005 NDS Table 11E, I get a Zperp of 450 lbs. Assuming all Adjustment factors are 1.0, is there something else that needs to be checked?
I ask because Woodworks Connection is telling me that the capacity of my connection is 157.9 plf, while reporting the controlling yield limit is 450 lbs, and all adjustment values =1.0. I can't figure out where it's getting the big reduction.
Any ideas?
Thanks,
Chuck