Hi Everyone,
I am designing a 240kV AIS substation for a utility client. Their standards and specifications specify a bus rating of 3000A. For flexible jumpers, I specified 2x2000 MCM ASC conductors to satisfy the ampacity rating. The client came back and told us not to use 2000 MCM conductors due to constructability issues. Apparently those conductors and too thick to easily bend and cause issues while installing shorter jumpers. After that comment, we have decided to go with 3x1590 MCM conductors but are having issues finding the right parts.
My question is:
In terms of constructability, will it be easier to install 3x1590 MCM conductors instead of 2x2000 MCM. Can anybody speak from their construction/design experience?
I am designing a 240kV AIS substation for a utility client. Their standards and specifications specify a bus rating of 3000A. For flexible jumpers, I specified 2x2000 MCM ASC conductors to satisfy the ampacity rating. The client came back and told us not to use 2000 MCM conductors due to constructability issues. Apparently those conductors and too thick to easily bend and cause issues while installing shorter jumpers. After that comment, we have decided to go with 3x1590 MCM conductors but are having issues finding the right parts.
My question is:
In terms of constructability, will it be easier to install 3x1590 MCM conductors instead of 2x2000 MCM. Can anybody speak from their construction/design experience?