Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

3.3kV Generator Grounding

Status
Not open for further replies.

SK07

Electrical
May 9, 2007
33
0
0
KW
In our Project we have On-site Power Generation with no "State Grid" Connection.

Power source is 2 nos. of 3.3kV Diesel Generators operating in parallel and 3rd 3.3kV Generator is connected but on standby mode.

My questuion is how Grounding is to be done for 3.3kV Generators oerating in parallel.

Also any International Standard that can be followed.
 
Replies continue below

Recommended for you

See, for instance : BS7430 Code of practice for Earthing
ch. 18.2.3 Generators which can operate independently of an incoming supply.
 
If you have the same generator size, it is allowed to make a Common Grounding Point because it is easy to applying selective relaying. Actually you can refer to IEEE 142 and ANSI C37.102
 