Hi All,
I am starting to commission a new chemical plant and have come across the following.
Motor Volts - 3300v
Motor FLA - 106A
Motor Protection - Gemstart 4
Normally I would accept the Earth Fault Setting from betwwen 10% - 20% of FLA, in this case approximately 10 - 20A.
We primary injected the Starter and the relay trips at 1A which equates to a 1% setting. On checking the documentation it was designed to this figure. We are able to increase the setting to 1.6A but no further without changing components. Has anyone got experience of settings this low and should I expect any nuisance tripping. The sensing device is a Core Balance CT and not 3 CT's residually connected. My intention is to increase the setting to 10% by changing the burden resistor on the CBCT, however please could you share experiences or your own standards on Earth fault setting on motors.
regards
UKEng
I am starting to commission a new chemical plant and have come across the following.
Motor Volts - 3300v
Motor FLA - 106A
Motor Protection - Gemstart 4
Normally I would accept the Earth Fault Setting from betwwen 10% - 20% of FLA, in this case approximately 10 - 20A.
We primary injected the Starter and the relay trips at 1A which equates to a 1% setting. On checking the documentation it was designed to this figure. We are able to increase the setting to 1.6A but no further without changing components. Has anyone got experience of settings this low and should I expect any nuisance tripping. The sensing device is a Core Balance CT and not 3 CT's residually connected. My intention is to increase the setting to 10% by changing the burden resistor on the CBCT, however please could you share experiences or your own standards on Earth fault setting on motors.
regards
UKEng