3 Ph.Transformer Backfeed

Status
Not open for further replies.

Plinko

Electrical
Oct 29, 2001
12
I'm looking for reference material on 3 phase transformer backfeed. For instants, I had a three phase bank 120/240 (gnd Y/closed delta...75/37.5/37.5 kVA) and lost one phase on the high side of the bank. Oddly enough, the phase that the cutout had isolated was actually at a higher voltage then other two phases. It's a classic delta backfeed situation. However, I'd like to show how this happens on paper (phasors, etc.)...for this and other TFR connections.
Thanks in advance....
 
Replies continue below

Recommended for you


See §4 of ANSI/IEEE C62.92.4-1991 …Application of Neutral Grounding in Electrical Utility Systems, Part IV—Distribution

For the described reason, it is listed in IEEE C57.105-1978 …Application of Transformer Connections… as a “problem connection” for it acts as a very good zero-sequence source on the wye side.
 