Navitech
Electrical
- Aug 30, 2003
- 3
I need to install an autotransformer lighting controller for a 120 VAC, 208 VAC and 277 VAC lighting circuits. Each controller will handle a 16 amp measured load which means I can combine circuits to a max of 16 amps. In each panel there is a common neutral for 3 hot feeds. I was told that on a three phase 4 wire breaker panel you must combine same phases. Phase A to phase A, B to B, C to C. For example if breaker 1 is phase A, 3 is phase B, 5 is phase C you cannot combine these because they are using the same neutral. Why not? NEC sect 220-22 states that the neutral feeder must be rated for the highest unbalanced load. What is the problem with combining phases? I can't find anything on the subject.
If breaker 1,3,5 each have 9 amps then the load on the common neutral is 0.
If breaker 1 is 4 amps, 3 is 8 amps and 5 is 15 amps...why can't you combine 1 & 3 which is 12 amps when the neutral is rated for the highest un balanced load of 15 amps anyway?
If breaker 1,3,5 each have 9 amps then the load on the common neutral is 0.
If breaker 1 is 4 amps, 3 is 8 amps and 5 is 15 amps...why can't you combine 1 & 3 which is 12 amps when the neutral is rated for the highest un balanced load of 15 amps anyway?