3-Phase 4-Wire Sub Panel panel form a 1-Phase Risidental Panel?

Status
Not open for further replies.

vaaoc1425

Electrical
Nov 14, 2006
25
I like to know whether it is technically correct to provide a 3-phase 4-Wire panel from a residential single phase panel which I assume which has L1 and L2 and a Neutral.

I was asked to provide a 60 amp sub-panel form a residential panel which I assume 100 Amp or larger. I had a choice of providing a 60 amp single pole breaker in the residential panel to feed the 60 amp sub panel OR provide a 30 amp three pole circuit breaker to feed the 60 amp sub panel.

I am confused as to whether it is technically correct in providing a three pole 30 amp circuit breaker to feed the 60 amp sub panel. The 60 amp sub panel may have five 20 amp circuits totals less then 40 amps. Unfortunately I didn’t have a chance to make a site visit to this moment.

Thank you in advance.

 
Replies continue below

Recommended for you

First off you can't get 3 phase from 1 phase without a rotary converter, so it is impossible. Next, why can't you feed the subpanel with a 2 pole breaker, this would be more appropriate.
 
Would not a two-phase breaker and a four wire cable with two "hot" leads, a dedicated ground lead and a dedicated neutral lead with separate ground and neutral buses in the sub-panel be correct?
 
The two hots on a 1 phase house service are 180deg out of phase. THERE IS NO SIMPLE WAY TO CONNECT THIS TO GET THREE PHASE POWER.

A 30amp 3ph circuit breaker should NOT be used from a 1ph panel to supply 60a 1ph load.

 
You better have an electrical engineer look at your project before you get into a jam.
 
My thread was a "what if", not that I was going to do it.
As I have indicated I also had choice of using a 1-pole 60 amp breaker to feed the sub-panel, which will work I am sure. Also as I have mentioned, I have not had a chance to verify the main panel in person, so the thread was again "what if"!

Thaks for all your info, I have decided to use a 2-pole 30 amp brekaer to feed the sub-panel. I am sure this will work.
 
One of my pet peaves;
Reversed polarity vs. 180 deg. out of phase.
When I hear the single, center-tapped transformer winding supplying a single phase service referred to as "180 deg, out of phase" I think that it is akin to calling two batteries in series, supplying 12 and 24 volts, "180 deg. out of phase" with each other.
respectfully
 
DC batteries do not have any 'phase'.

Have you got a better way to shorthand explain the split-winding grounded-center-tap one-phase connection?
 
Semantics, semantics...

Is 'The two hot lines are in anti-phase' any better?



----------------------------------
image.php
Sometimes I only open my mouth to swap feet...
 
Weren't there Star Trek episodes where people were in "anti-phase" realms, right next to everyone else but unseen and unable to interact?




Am I coming off and a Trekkie geek?
 