I would like someone to verify an engineers calculations:
I have a delta / Y-grounded 45 KVA-3phase 480-208/120V transformer.
I calculate the rated line current at I primary @ 54.12A and I secondary @ 125A. The individual phase current should be Ip = 54.12/sqrt(3) = 31.25A and Is = 125A. The individual feeders are sized according to the phase current correct? Is this the obvious conclusion, I want to be sure? The secondary feeders (Al) are going to be like 500 feet long! (outside in winter though)
Thanks for the help.
I have a delta / Y-grounded 45 KVA-3phase 480-208/120V transformer.
I calculate the rated line current at I primary @ 54.12A and I secondary @ 125A. The individual phase current should be Ip = 54.12/sqrt(3) = 31.25A and Is = 125A. The individual feeders are sized according to the phase current correct? Is this the obvious conclusion, I want to be sure? The secondary feeders (Al) are going to be like 500 feet long! (outside in winter though)