- Aug 3, 2011
- 57
I am a bit rusty with 3 phase calculations and I was hoping I could get some input.
In calculating current for 3 phase the equation is I=VA/(V*1.73) [not taking into account PF]. If you have a 3 phase wye distribution, does this then give you the current traveling through each phase-to-neutral?
When calculating voltage drop in conductors smaller than 1/0, the equation is Vd=(1.732xKxIxD)/CM. I have 2000KVA transformer with a 480V 4 wire wye secondary, and the documents call for 8 conduits with 4#600kcmil wires would I take 2000KVA/(1.73x480) and up it 15% since the transformers are outdoor padmount to get approx. 2700A. Would I then divide that current by 8 to get approx 337A for each wire (assuming all the wires are the same length)? If I then used that in the above voltage drop calculation, would that be the voltage drop on each wire for each phase?
Please be gentle i'm a new, junior engineer
David
In calculating current for 3 phase the equation is I=VA/(V*1.73) [not taking into account PF]. If you have a 3 phase wye distribution, does this then give you the current traveling through each phase-to-neutral?
When calculating voltage drop in conductors smaller than 1/0, the equation is Vd=(1.732xKxIxD)/CM. I have 2000KVA transformer with a 480V 4 wire wye secondary, and the documents call for 8 conduits with 4#600kcmil wires would I take 2000KVA/(1.73x480) and up it 15% since the transformers are outdoor padmount to get approx. 2700A. Would I then divide that current by 8 to get approx 337A for each wire (assuming all the wires are the same length)? If I then used that in the above voltage drop calculation, would that be the voltage drop on each wire for each phase?
Please be gentle i'm a new, junior engineer
David