mrg397cs
Electrical
- Sep 23, 2003
- 9
The normal line to ground capacitive charging current for one phase is the line to neutral voltage divided by the capacitive reactance in ohms. Let's assume that each phase has a current of one amp when the system is unfaulted ( Ia +Ib +Ic = 1). When one of the phases is grounded, the total system charging current is 3 times normal phase to ground current.
During a fault on one of the phases in a feeder, and the voltage on the other phases stepped up 1.73 times line to neutral, will a zero sequence current transformer/detector on the feeder see 1 amp or 3 amps charging current?
During a fault on one of the phases in a feeder, and the voltage on the other phases stepped up 1.73 times line to neutral, will a zero sequence current transformer/detector on the feeder see 1 amp or 3 amps charging current?