3 Phase Generator on Single Phase Service

Status
Not open for further replies.

GigawattClub

Electrical
Dec 8, 2004
4
I have a 50kW 3 Phase 120/240 12 Wire Synchronous hydro generator which I want to install at a site that only has single phase service available from the utility.

Has anyone done something like this in the past? Can the machince be de-rated to a safe level and run with only one phase connected? At what level will the unbalance cause damage to the generator?
 
Replies continue below

Recommended for you

Yes,yes.
Properly connected, 2/3 of the original KVA rating. Typically the KW will equal the KVA with an allowable PF of 100%
Search this site.
This topic has ben covered extensively here in the last few months.
If you still have questions, by all means ask, but please do some research first.