I am intending to connect 9 2kw metal halide lights so that they are balanced over the 3 phases. The supply voltage is 400v between phases. This will mean that the load is balanced with 3 lights connected in paralell across each phase. This will bean that there is 6kw connected between phases. I want to know how to calculate the current taken from each phase of the supply. I do not know the power factor of the lights. Any help would be greatly appreciated.
Thanks in advance.
 
Replies continue below

Recommended for you

Its simple.

If the load is evenly divided between the three phases, the total load is 18kW (3*6kW).

For a balanced three phase load, Line Current I= (18kW/p.f.)/[(SQRT (3))*400] in each line.

where kw/p.f.= kvA.

Or you can say voltage per phase is 400/sqrt 3 =230V

Current for each phase = kva per phase/voltage per phase
=(6kW/p.f.)/230. Either shall result in the same current value.
 
Thanks rbulsara, that's exactly what I was looking for
 
One correction:

I forgot the factor of 1000. Multiply kVA*1000 to get VA.

(or use voltages in kV).
 
Suggestion: The current may need to be increased a little bit since there will probably be ballasts that will increase the 2kW to some higher value depending on which type of ballast is applied.
 
Thanks jbartos,
I got the power factor rating of the ballast from the lighting manufacturer and I have sorter out the problem.
Thanks to all for your helpful replies.
 