andstef
Electrical
- Oct 12, 2002
- 4
I repeat my question because of misunderstandings.
I have one 3-phase motor of SIEMENS designed for the following parameters:
50Hz/500V/0,75kW/1,92A/2855rpm///575V/60Hz/0,86kW/1,96A/3455rpm
The same motor can work either with 500V/50Hz or 575V/60Hz
But in the reality I have rated voltages in the mains 400V/50Hz (Europe) or 480V/60Hz (U.S.).
Parameters on the motor refer to 500V or 575V. Firstly I do not understand why 500V or 575V (in which country there is 575V in the mains?). There would not be this question if had above mentioned parameters referring to 400V (Europe) or 480V (U.S.).
My questions:
1. What coarse values of power, speed, current would have this motor by 400V/50Hz in comparison to 480V/60Hz?
2. Can I use the same circuit-breaker (2A) for this motor in Europe as in in the U.S. I afraid not, because of different currents.
I have one 3-phase motor of SIEMENS designed for the following parameters:
50Hz/500V/0,75kW/1,92A/2855rpm///575V/60Hz/0,86kW/1,96A/3455rpm
The same motor can work either with 500V/50Hz or 575V/60Hz
But in the reality I have rated voltages in the mains 400V/50Hz (Europe) or 480V/60Hz (U.S.).
Parameters on the motor refer to 500V or 575V. Firstly I do not understand why 500V or 575V (in which country there is 575V in the mains?). There would not be this question if had above mentioned parameters referring to 400V (Europe) or 480V (U.S.).
My questions:
1. What coarse values of power, speed, current would have this motor by 400V/50Hz in comparison to 480V/60Hz?
2. Can I use the same circuit-breaker (2A) for this motor in Europe as in in the U.S. I afraid not, because of different currents.