I have a question for the NEC gurus here...
We have an application where we use .5 and 1HP motors. They are controlled by 3-Phase CRYDOM relays. We provide the customer with pigtail connections to the relay where they will hook up their 3-phase, 3-wire power when the unit is installed.
I was asked to clean up our (old) wiring hookup diagrams and I noticed that our diagram only shows fuses on two of the 3-phase supply leads coming from the customer side of the relay. I questioned the tech about this as it seemed to me that each phase should be fused, not just two. His answer was that in the U.S., only two phases need to be fused.
I looked this up in our (1996, unfortunately) NEC book and section 430-36 states that each conductor shall be fused. Can someone clarify this for me?
TIA
We have an application where we use .5 and 1HP motors. They are controlled by 3-Phase CRYDOM relays. We provide the customer with pigtail connections to the relay where they will hook up their 3-phase, 3-wire power when the unit is installed.
I was asked to clean up our (old) wiring hookup diagrams and I noticed that our diagram only shows fuses on two of the 3-phase supply leads coming from the customer side of the relay. I questioned the tech about this as it seemed to me that each phase should be fused, not just two. His answer was that in the U.S., only two phases need to be fused.