jpr2004
Mechanical
- Sep 13, 2004
- 3
First the history. I have an older 7.5 hp 3 phase 220V motor that I need to power in my shop at home. I have looked at the VFD, but at this hp level they are require a 3 phase input, not single phase. This has me lead to build a RFC. The idler motor that I had planned on using was toasted, so for testing this weekend I used a 3 hp motor as the idler motor with the 7.5 hp motor turning a variable speed transmission and two separate gear boxes without any load applied.
These are the measurements that I recorded during testing which make no sense to me. Measurements were made with a Fluke 30 clamp on amperage meter and Fluke 73III voltage meter.
Single phase from breaker panel
L1 current is 8.1 amps
L2 current is 8.3 amps
L1-L2 voltage is 245
3 phase to the 7.5 hp load
L1 current is 10.5 amps
L2 current is 10.4 amps
L3 current is 10.9 amps
L1-L2 voltage is 245
L1-L3 voltage is 245
L2-L3 voltage is 244
L1-L3 capacitor bank is 120 mfd
L2-L3 capacitor bank is 70 mfd
L1 current at 3 hp idler motor is 2.5 amp
L2 current at 3 hp idler motor is 2.6 amp
L3 current at 3 hp idler motor is 2.8 amp
Checking the in coming power meter indicates that running the central a/c at 19.5 amps is pulling nearly four times the amount of power than the RPC and the 7.5 hp motor.
It appears to me that since my idler motor is so small, that I have basically made half a static convertor and half a rotary convertor. But this does not explain the measured in coming current being less than the measured load current with the voltage equal.
These are the measurements that I recorded during testing which make no sense to me. Measurements were made with a Fluke 30 clamp on amperage meter and Fluke 73III voltage meter.
Single phase from breaker panel
L1 current is 8.1 amps
L2 current is 8.3 amps
L1-L2 voltage is 245
3 phase to the 7.5 hp load
L1 current is 10.5 amps
L2 current is 10.4 amps
L3 current is 10.9 amps
L1-L2 voltage is 245
L1-L3 voltage is 245
L2-L3 voltage is 244
L1-L3 capacitor bank is 120 mfd
L2-L3 capacitor bank is 70 mfd
L1 current at 3 hp idler motor is 2.5 amp
L2 current at 3 hp idler motor is 2.6 amp
L3 current at 3 hp idler motor is 2.8 amp
Checking the in coming power meter indicates that running the central a/c at 19.5 amps is pulling nearly four times the amount of power than the RPC and the 7.5 hp motor.
It appears to me that since my idler motor is so small, that I have basically made half a static convertor and half a rotary convertor. But this does not explain the measured in coming current being less than the measured load current with the voltage equal.