Hello nmark
Glad to here that you're up and running.
It is very possible that the faulty drive was grounded internally and pulling the voltage to ground down on one phase.
There are, however some safety related inconsistencies that you may want to check.
It would be well to inquire or investigate whether the system is solidly grounded or resistance or impedance grounded.
It is probable that the drive was faulty and was responsible for pulling the voltage to ground down. The voltage readings may be acceptable with a resistance or an impedance grounded system.
However, it would be well from a safety viewpoint to check the point to which you measured the 70 volts to ground. You may have a piece of equipment with a poor ground connection.
If you have a solidly grounded system you definitely have some faulty grounding connections. This is why I am suggesting a little more investigation even though the equipment is working well.
If you get a chance to look inside the failed drive, let us know if the failure is obvious.
itsmoked (Electrical)
7 Mar 06 23:09
I'm betting the brass dust won... Easily.
This was a good suggestion and some of us are wondering if it was the case.
The poor mans solution to checking ground continuity is to use a dry type transformer for isolation and an electric appliance for a load. An electric kettle works well. You want something that draws about 8 or 10 amps. The isolation transformer should be suitable for the load, i.e. 1000 VA or more. A 2-pole breaker is a nice safety feature. Run 120 volts (or your normal appliance voltage depending where in the world that you are.) from the transformer to the breaker.
From the transformer connect to the appliance and from the other lead of the appliance connect to the point that you used for your ground measurement. Now go back to a point on the system where you are sure that you have a good ground.
CAUTION. You are testing a possibly faulty circuit and there may be a surface voltage on the equipment during this test, (But not nearly as much as when you had the 70 volt reading from the 480 volt system.)
Your appliance current should now be flowing from the transformer through the circuit breaker to the appliance. From the other connection of the appliance the current will flow to the ground connection. The current will follow the grounding path to the other point of connection to the ground system. From the second ground connection the current will return to the breaker and from there to the transformer.
The voltage across the ground path should be close to zero. A voltage of any magnitude indicates a bad connection in the grounding circuit. You can locate a bad connection by measuring voltages "point to point". Use a long jumper to connect one end of your volt-meter to the first ground connection and start measuring voltages along your grounding path. The voltage should be almost zero and a bad connection will be isolated by a jump in voltage from one point to the next. You can follow the current with a clamp ammeter.
yours