Sorry if this seems like a simple question to this group, but I am struggling with this.
We have an instrument that we are planning to run on single phase power. In the past the manufacturer has only used unbalanced 3-phase (Wye) configurations. They just use the three phases and the neutral to run three groups of devices. One of the service engineers tells us that when he measured current in each leg of the Wye he got something like 22A, 11A, and 7A, and that therefore we have to expect around 40A if we run on single phase. However, logic tells me this should actually be divided by (3)^0.5, and that we therefore should expect under 25A.
Whose right?
We have an instrument that we are planning to run on single phase power. In the past the manufacturer has only used unbalanced 3-phase (Wye) configurations. They just use the three phases and the neutral to run three groups of devices. One of the service engineers tells us that when he measured current in each leg of the Wye he got something like 22A, 11A, and 7A, and that therefore we have to expect around 40A if we run on single phase. However, logic tells me this should actually be divided by (3)^0.5, and that we therefore should expect under 25A.